# Probleme E/S conflit

**URL:** <https://community.factoryio.com/t/probleme-e-s-conflit/4497>\
**Category:** Support\
**Created:** [January 13, 2026, 2:53pm UTC](https://community.factoryio.com/t/probleme-e-s-conflit/4497 "2026-01-13T14:53:44Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![user47](https://avatars.discourse-cdn.com/v4/letter/u/edb3f5/32.png) [@user47](https://community.factoryio.com/u/user47)\
**Post date:** [January 13, 2026, 2:53pm UTC](https://community.factoryio.com/t/probleme-e-s-conflit/4497/1 "2026-01-13T14:53:44Z")

</div>

Hello, I’m using TIA Portal v16 + MHJ-PLC-Lab-Function-S71500. My project has 47 inputs, 95 outputs, and 15 analog I/O pins. My problem is that some of my inputs work in TIA, but others don’t return from the factory IO. I thought I saw online that it was possible to increase the number of inputs/outputs in MHJ-PLC? Is that true? If so, how do I do it?

---

<div class="post-metadata">

**Author:** ![adriana.silva](https://dub1.discourse-cdn.com/flex017/user_avatar/community.factoryio.com/adriana.silva/32/752_2.png) [@adriana.silva](https://community.factoryio.com/u/adriana.silva)\
**Post date:** [January 13, 2026, 4:45pm UTC](https://community.factoryio.com/t/probleme-e-s-conflit/4497/2 "2026-01-13T16:45:37Z")

</div>

Hello @user47,

Welcome to the forum!  
This is an international forum, so I’d like to kindly ask you to write your posts in English, please.

---

<div class="post-metadata">

**Author:** ![adriana.silva](https://dub1.discourse-cdn.com/flex017/user_avatar/community.factoryio.com/adriana.silva/32/752_2.png) [@adriana.silva](https://community.factoryio.com/u/adriana.silva)\
**Post date:** [January 15, 2026, 9:38am UTC](https://community.factoryio.com/t/probleme-e-s-conflit/4497/3 "2026-01-15T09:38:59Z")

</div>

Hello @user47,

Thank you for translating your post!  
I’m sorry, I’m not sure I understand your setup, so I’d like to ask a few questions so that I can help you.  
By saying that you are using the MHJ-PLC-Lab-Function-S71500, do you mean that you are using the template available on our documentation page?  
From what you describe, I assume you are using PLCSIM. Is this correct?  
Could you please share some images of your issue? The driver configurations in Factory I/O as well as the configurations of the PLC might be helpful.

---

<div class="post-metadata">

**Author:** ![user47](https://avatars.discourse-cdn.com/v4/letter/u/edb3f5/32.png) [@user47](https://community.factoryio.com/u/user47)\
**Post date:** [January 18, 2026, 1:36pm UTC](https://community.factoryio.com/t/probleme-e-s-conflit/4497/4 "2026-01-18T13:36:09Z")

</div>

![page1](https://europe1.discourse-cdn.com/flex017/uploads/factoryio/original/2X/7/79329abbb5303958cfd4522d17f6f64458269569.png)

 ![page2](https://europe1.discourse-cdn.com/flex017/uploads/factoryio/original/2X/a/ab418a79c37c16c1e2be40218e15734f62694db0.png)

---

<div class="post-metadata">

**Author:** ![adriana.silva](https://dub1.discourse-cdn.com/flex017/user_avatar/community.factoryio.com/adriana.silva/32/752_2.png) [@adriana.silva](https://community.factoryio.com/u/adriana.silva)\
**Post date:** [January 19, 2026, 9:41am UTC](https://community.factoryio.com/t/probleme-e-s-conflit/4497/5 "2026-01-19T09:41:31Z")

</div>

Hello @user47,

Thank you for the images, they were very helpful!

It seems like you have some addresses that overlap.  
You have I4.0 and an ID4 set in Factory I/O. This means that both tags are trying to write to the same address. To solve this, you’ll have to set the analog inputs to start at 6 so that they don’t overwrite any of the digital inputs.  
However, PLCSIM has some limitations when it comes to the number of I/O points you can have. If Factory I/O doesn’t let you set a higher offset, try to reduce the Count.

I hope this helps.