Factory IO connected successfully to PLSIM V20 but simulation does not work

Hello, I have a problem with my Factory IO, I connected it successfully to PLCSIM V20, but when I tried to play the simulation it did not response, I have buttons and conveyor, my scenario is when I press the button the conveyor must work but it did not

Hello @mohabur0909,

Welcome to the forum!
In the image you shared, I see that Factory I/O’s scene is not running. When you say you tried to play the simulation, but it didn’t respond, what exactly do you mean? Did you press play in Factory I/O?
Everything else in the image you shared seems okay, so from my understanding, it should work.

Yes when I pressed the play button, when I press a button there is no action or response from any output, maybe there is an error in the code, but when I opened my TIA Portal and turned on my monitor there is also nothing happen when I press the buttons in factory io

is the situation clear now ?

In Factory IO you are using I0.0 for Start and I0.1 for Stop, but in TIA-Portal I see I10.0 and I10.1. The Adresses have to be the same on both sides