Hi @thasamm,
Are you using SP16 or higher? If so, CODESYS suffered some changes, so try this:
-
Check the “Discrete Bit Areas” box under ModbusTCP_Slave_Device > General > Configured Parameters and write the number of Coils and Discrete Inputs you need, as shown in the image below.
-
Map the variables (using Coils and Discrete Inputs).
-
Map these variables in FIO.
We’ll release a tutorial regarding these alterations. Meanwhile, let me know if this worked for you.