factory io inputs do not arrive correctly in tia portal
Some come and some don’t what can i do?
How does your setup look like? Do you perhaps have physical hardware that might overwrite the Factory IO in- and outputs?
I have same problem specially after default input points from i0.0 to i1. 7 after that the feedback is uncorrect
Is there a solution?
I have a problem in connection between tia and factory io
The default point in factory from i0. 0 to i1. 7 are perfect
If i add some input points there is problem in connection
Is there a solution for that?
If the input in factory is true, it appears in tia flashing between true and faulse and is not Completely true
Hello @mahmoudbnkhalifa1234
Welcome to the forum!
The flashing behavior you describe is usually caused by overlapping addresses from Factory I/O and a physical PLC. The PLC inputs will overwrite Factory I/O’s inputs, as Janbumer1 mentioned above.
Are you using a physical PLC? If so, to solve the issue, we recommend offsetting the inputs’ addresses either on the PLC or in Factory I/O. To do so in Factory I/O, select the driver you want to use and set the offset you want on the configuration page.